3

Why are we still cutting grounds so short on new construction with 312 deep boxes when it causes issues and extra work for troubleshooting?

Asked by Ethan Le Gall
4 months ago
Last Updated: August 7, 2024

What’s the deal with cutting the grounds so short on new construction with 3-1/2” deep boxes? It’s just something that bugs me, especially when there’s a problem and I have to yank out a box for troubleshooting. I know it used to be necessary back in the day when boxes were smaller, but why still do it now?

Related picture 1Related picture 2
Subscribe
Notify of

283 Comments
Oldest
Newest Most Voted
Inline Feedbacks
View all comments
Dilara Van Hoogdalem

I still have the codes and will use them if needed. They’re still more valuable than useless wegos.

Dilara Van Hoogdalem

I usually cut them a bit longer than the box. And yes, only with the grounds. I think it’s required by code if you use them. I’ll have to look it up. But that’s how I was taught as well. 😂

Dorina Ruoff

This install violates code

Camille Wilson

Ever heard of NEC 300.14?

Koen Huinink

Um that is for conductors

Vicenta Navarro

Just to clarify, the crimp is considered a splice, and the shorter conductor is essentially being extended by the longer one it’s connected to.

Dorina Ruoff

The 2023 NEC actually got updated to allow splicing of the required free conductor. This change was aimed at addressing existing installations where conductors were shortened during device replacements. It wasn’t meant to encourage sloppy work in new installations. Would you intentionally cut both grounded and ungrounded conductors to 2 inches and then splice a pigtail? Technically, it might pass 300.14… Oh, and let’s not forget about 110.12. I wouldn’t hesitate to call out this subpar work.

Francis Robert

Just a heads up – grounds are not considered conductors. I always keep my wires at 6 inches, even the grounds.

Dorina Ruoff

Hey, talking about equipment grounding conductors here.

Vicenta Navarro

Hey, it’s not my argument. It’s all about the code. If you’re not a fan of it, suggest a change to the code-making panel. The code sets a minimum standard, but we can always strive for better. By the way, I highly recommend watching Mike Holt’s DVDs. They are definitely worth the investment of both money and time. You’ll gain a lot of knowledge and elevate your understanding of the code.

Vicenta Navarro

I’m not “interpreting” anything. The length extending out of the box should be 6”. Even if there’s a splice in that conductor, it’s still following the code. Would I personally do that? No. Is it code-compliant? Yes.

Vicenta Navarro

You raised the question, and I’m giving you an answer. They do it because it’s permitted. If you’re not a fan, it’s irrelevant.

Why are you taking out boxes for troubleshooting? In what situation would having longer free conductors spare you from box removal?

علی رضا نكو نظر

Bad electricians passing on bad practices. Using wire nuts and pigtails. round crimps are a sloppy shortcut.

Norisete Silveira

Definitely not slacker!
The ground connected to the device is NOT CUT.

NO RISK OF FAILURE

Norisete Silveira

This photo is a terrible installation.

If you really like wire nuts, they do make green ones that don’t need the ground to be cut!

Norisete Silveira
Norisete Silveira

You’re not taking your work seriously.
Educate yourself on “continuous ground”
And “Irreversible ground”

The most basic thing in residential settings is a whirlpool bath tub.

If you’re not knowledgeable about grounding… refrain from making comments about it

Norisete Silveira

It’s a weak point 🤦‍♂️

علی رضا نكو نظر

It was doomed from the moment it was done. Having to redo poor quality work is frustrating. Consider the next person who has to deal with it, instead of rushing through the job.

علی رضا نكو نظر

Just a simple, cost-effective method. Nothing more. No need to stress about a weak connection with wire nuts. If you’re skilled, wire nuts work fine. Crimps are just a convenient option for those who prefer efficiency over everything. There really isn’t a strong case for using them. It’s common knowledge that they’re not reliable.

Norisete Silveira

You’ll find it amusing when you spend 3 hours searching for an available ground

Norisete Silveira

Search it up trunk boy

علی رضا نكو نظر

That’s never gonna happen. Hasn’t in the past 20 years. Hack.

Didrik Abdulla

Junkkkkkkkkkkkkk

Norisete Silveira

“Love is love”
….. are you suggesting something questionable?

Norisete Silveira

Not a fan of inspections, huh?

20 years and counting, right? 👌

علی رضا نكو نظر

Failing them isn’t the best idea.

علی رضا نكو نظر

You’re being quite foolish.

Darío Cornejo

I prefer using a green wire nut and leaving one ground a bit longer. I find those crimps useful only in tight boxes where every inch matters, like with bulky switches. They’re great for saving space. I just dislike when the ground wires are cut too short.

علی رضا نكو نظر

I’d rather not deal with those. Most people avoid them. They’re a pain for service work. It also varies depending on your employer. Some companies (usually the cheaper ones) require their use. However, every reputable company I’ve worked for doesn’t use them at all.

Askold Sobchuk

When I started out we used green wire nuts, but I was always told to make sure not to trim the wires too short. Leave them with at least one fold.

Kaya Yılmazer

I’m still sticking with greenies haha, haven’t come across anything better yet.

Rose Fontai

In order to conserve space, that’s why they’re secured tightly with a pigtail.

Rose Fontai

Just to maintain consistency

Katherina Kortmann

This goes against NEC regulations, so…

Rose Fontai

When did this happen? I see it everywhere I go.

Katherina Kortmann

I’m not exactly sure about 300.14, what year was that?

Anitha Banerjee

I prefer using greenies for the grounds, the inspectors always want to see them around here but personally, I like splicing the ground together and tailing off, especially in switch boxes. It bothers me when they leave one long ground

Stine Svela

I see your point and I’m guilty of using them, but I still prefer to use deep metal boxes for old work with Madison bars.. haha

Darío Cornejo

Are you in a residential area?

Stine Svela

Yes indeed

Darío Cornejo

Why do you live there, ? Is that the area code for your location?

Bently Addy

I personally use wire nuts and make sure to leave 6″ of conductor, unless the box is deeper than 3 1/2 inches, in which case 3″ is sufficient. I leave enough conductor for the next person as required by the code.

Ümit Gürmen

Hey Ryan, you really opened my eyes to something. I now understand why many guys prefer 18 cubic inch boxes over 14 cubic inch boxes. It allows for more space and depth for the 6-inch connectors. I did some calculations on the potential extra cost of using more copper compared to the price variation in boxes. It definitely makes sense for the larger setups.

Roland Wells

I prefer to have one ground wire extending at least 6 inches past the box opening, even though technically 3 inches is enough. It just makes it easier to fit all the wires in neatly.

Catherine Rousseau

Hey Armando! For NEC compliance, all box wires should be either 6 inches from the entrance or 3 inches past the face of the box. Unfortunately, this installation does not meet those guidelines.

Roland Wells

I always place them about six inches from the front of the box, then extend them three inches past. ood luck with your connections, and if you ever need to replace it in the future 😳🙄.

Catherine Rousseau

NEC 300.14 requires wires to be at least 6 inches from where they enter the box. It’s always good to have more space if possible, but keep in mind that larger devices like USB receptacles, FCIs, or dimmers might need more room.

Roland Wells

Hey, we should update the code because it’s not good. Over time, switches, plugs, and wires will need to be replaced, and the wire will get shorter. Can you imagine? 😳🙄

Catherine Rousseau

Most of the time, you’ll likely need to pigtail for receptacles since they’re usually jumpered through the boxes.

Roland Wells

I totally agree. Over time, outlets and switches tend to be replaced, and sometimes wires end up breaking during those changes, requiring redoing them. 🙄

Roland Wells

If it’s just two wires coming in and two going out, you can simply wrap them around the screws on the outlets, tighten them, and you’re good to go. No need for all that cutting.

Catherine Rousseau

Oh yeah, that’s probably only about a quarter of them. I’d suggest leaving longer wires if there’s just one set in the box! 😂

Roland Wells

You know, when it comes to electrical work, I try not to overload my boxes. Typically, I only deal with two sets of wires – one coming in and one going out on outlets.

Catherine Rousseau

If you have 2 sets, then you should pigtail and your argument becomes irrelevant. Just replace the pigtail if it gets too short.

Roland Wells

I already mentioned to wrap them around the screws and you’re good to go. On the ground, you can use a crimp sleeve and that’s it. It seems like you haven’t been doing electrical work for very long, unlike me, with 40 years of experience as a licensed contractor in California, trained by the best

Catherine Rousseau

I can’t believe you use the *device* as the connection instead of properly pigtailing, and you’ve been doing that for 40 years? 😭

Roland Wells

Wrap around the screw instead of behind the outlet hole, do you realize how much time you waste pigtailing everything compared to just wrapping around the screw 😳

Roland Wells

I think you might benefit from some retraining as you seem to be wasting time and wire nuts, not very cost-effective 🙄🤣🤣

Catherine Rousseau

That sounds terrible. 🙁 I hope you can retire soon

Roland Wells

I hope your boss doesn’t end up broke with the way you work! 😂😂

Roland Wells

Have a great day, rookie! 😄

Catherine Rousseau

I think the US code still allows it for residential areas. In Canada, pigtails have been required since 2012.

James Chavez

A waygo would definitely be a quick fix for this, especially just for a ground wire.

Catherine Rousseau

I hear you, but it’s still not up to code.

مهدي مرادی

Hey, just a heads up, using an outlet as a pass through/junction is not recommended.

Catherine Rousseau

I’ve been working in commercial electrical for almost 20 years and using the device as the junction hasn’t been allowed by code in Canada for commercial that entire time and for residential for over 12 years. I guess the US is just behind on yet another fire hazard with their code revisions.

Ingolf Vogelsang

🤨 would you do the same in a plastic box???🤨

Diana Kelley

This is exactly where I like to use them.

Gojko Sekulić

So you’re daisy chaining every outlet. Instead of pigtailing and allowing it to be a parallel circuit, you’re wiring everything in series so when one outlet goes out, everything downstream goes out too.

I would much rather pigtail

James Chavez

How about changing out that solid bare for some insulated ground? That’s the only thing that bothers me about residential – the bare ground on the devices.

Diana Kelley

It is what it is. There’s never an insulated ground using NM.

James Chavez

In the past, they used to include an insulated ground in some of the romex. I have observed it in some older residences.

Roland Wells

What are you on about no parallel wiring we’re not connecting Christmas lights 😳🙄🤣🤣

Roland Wells

The sole way that could occur is if someone damages an entire outlet that will disrupt the circuit otherwise that will occur in years 😳🙄🤣

James Chavez

Josh I have no idea what you find amusing but it seems you’ve never encountered romex with an insulated ground.

Gojko Sekulić

Not in the slightest. You believe outlets never malfunction on their own?

Kaitlin Lopez

How frequently do you reckon individuals switch devices?🤣

Roland Wells

I’ve had experience working in high-end places like Beverly Hills and Bel Air. It’s interesting to see the different styles and colors that change every few years, from regular to decorative including switches. Pretty cool, right?

Julius Pulli

What’s the issue with having bare ground?

Wolf-Dietrich Helfrich

40 years? I highly doubt that. I’ve been in the trade for 9 years and I can tell this is not up to standard. ood luck fixing all your previous work.

Roland Wells

Hey, I’m actually a licensed contractor in California since 1992. Just wanted to clear that up.

Wolf-Dietrich Helfrich

You seem to have been struggling with your work since 1992. It’s good to be aware of that lol.

Roland Wells

Hey, no need to be rude. Can you please go grab the wire stretcher? 🤣🤣🤣

Mücahid Mourik

Not exactly, check out the exception at the end of the rule. If there are ground screws in the box, only the one connected to the outlet or switch needs to be 6” long

Mücahid Mourik

That approach wouldn’t be accepted in Canada. For an in and out circuit, pigtails are necessary to prevent interruptions to other outlets on the circuit

Roland Wells

Ryan erald in commercial settings, we only use pigtails to avoid disrupting business activities. But in residential work, it’s fine to do it that way

Catherine Rousseau

Ryan erald the exception is specifically for conduit and wires passing through the JB without splicing. When 2 ground wires are spliced together, that’s considered a junction

Mücahid Mourik

I heard you guys have different plastic boxes down there. Ours come with two ground screws. You can run 4 separate lumex’s into it without splicing the grounds

Mason Gregory

Hey, make sure all the ground wires stick out at least 3” from the box to meet code requirements

Roland Wells

I like to keep the wires about 6 inches away from the box’s face because it helps with connecting and rolling them in once the other wires are attached.

Mason Gregory

I hear what you’re saying – so basically, when you have 3 wires and you crimp them 3″ outside the box, one of them ends up being around 6″ to connect to the receptacle while the other two are just 3″. You don’t measure them exactly, you just estimate 3″ which might be slightly more.

Roland Wells

That sounds great, I like to crimp my grounds right at the front of the box so they are barely crimped and leave about three or four inches out from the front.

Roland Wells

I always make sure to keep my hots and neutrals 3 inches from the face when wiring in outlets. I leave them 6 inches from the face of the box for easy access later on since outlets tend to get changed over the years. Thinking ahead for the next person who might need to replace them, whether it’s in a few years or even 10 or 15 years down the line.

James Chavez

It’s best to troubleshoot circuits while they are still hot, otherwise you risk running into potential dangers. Trust me, .

James Chavez

Sure thing, ! You can actually do that. The outlets are rated for pass-through as long as there is only one wire per screw.

مهدي مرادی

Yeah I know, unfortunately lol. I think it should be standard practice for them to be pigtailed so as not to disrupt the rest of the circuit when replacing a receptacle or when one malfunctions 🤷🏼‍♂️

James Chavez

Brooks Most failures occur with backstabbed devices under a heavy neutral load

مهدي مرادی

Yeah, lots of people are backstabbing and it’s pretty disgusting haha

James Chavez

Yeah

Oliver Luoma

Doing things by running the load from an entire circuit through each device as you go is not the best approach. If you consider a couple of extra minutes and a couple of wire nuts a waste of time, I kinda hope you’re retired by now.

Roland Wells

Hower let me share something with you I was a contractor since 1992 I did many many jobs never had one call back so there you go 😀

Roland Wells

Hower the evidence is in my quality work I don’t do shoddy work maybe you do maybe other people do I don’t get call backs 🤣

Oliver Luoma

That’s fantastic. It’s still not a good idea to run the full load of any given circuit through each individual device. You are definitely entitled to your opinion, have a wonderful day.

Roland Wells

Hower in the US and California you can do it that way for residential you wrap it around the screw there’s a solid piece of metal that connects the two. I don’t do that in commercial commercial I always pigtail because it’s a business they can’t be interrupted by me shutting the power off and all that have a good day

Oliver Luoma

I never mentioned it couldn’t be accomplished I just think it’s not a good idea.

Roland Wells

Hower well that’s okay that’s your perspective but I prefer saving on the labor and all those wire nuts and time to do all that it’s residential it’s not commercial it’s not industrial you won’t have a call back

Oliver Luoma

I think it’s wonderful that you do whatever works for you. Complaining about such a tiny percentage of the total installation cost just doesn’t add up to me. And even if you claim not to have callbacks now, eventually, you will encounter burnt-up receptacles on your installations. And when that happens, you’ll end up losing the entire circuit, not just the problematic receptacle. If you’re willing to cut corners and work that way, it’s entirely up to you.

Oliver Luoma

Also, if you’ve ever run a receptacle circuit as a multi wire branch circuit and had the conductors passing current through the receptacle, that’s a violation of the code.

Roland Wells

Hower If you get yourself a large number of track homes – let’s say 100 units or even a thousand units – as a contractor like myself, you understand the cost-effectiveness of doing things my way. Just accept it – you do it your way, and I’ll do it mine.

Oliver Luoma

Absolutely, money over quality, right?

Roland Wells

Hower Oh yeah, if I don’t prioritize quality, why haven’t I received any callbacks? 🤣🤣

Oliver Luoma

O ahead and do whatever brings you joy. It’s unlikely that you’ll find many people who share your perspective.

Roland Wells

Hower, you know what I’ve learned over the years? It’s essential to not give a s*** about what anyone else thinks 😳🙄🤣🤣

Princess Van Renswoude

😂, my friend, you still have a lot to learn!

Oliver Luoma

Over the years, I’ve found that people who make that claim usually aren’t the greatest folks around. You’ve made it pretty clear that you prioritize money over quality, and I understand.

Roland Wells

Well let me just say, boy, I was in Baghdad before you were even in your Dad’s bag 😳🤣🤣, which means I’ve been doing electrical work before you were born. You really don’t know much at all 😂

Roland Wells

Hower, it seems like I must be living in your head because you just can’t seem to get over it, can you? Maybe you should consider therapy, but first, let’s have a beer and relax. Stop trying to get to me, none of you will be able to get under my skin 😳🤣🤣

Princess Van Renswoude

🤡 hey, remember to stick to your 3-inch rule! Oh, and by the way, your mom likes my bag!

Roland Wells

You’re so clueless you don’t even know what you’re talking about, you probably never worked a day in your life in electrical work, buzz off

Princess Van Renswoude

You should have stayed in your country !
o back and pull some 3” wires

Roland Wells

I just clicked on your profile to see if you look as silly as you sound 😂😂

Princess Van Renswoude

Buddy let’s compare bank accounts !
o back to baggerdad

Roland Wells

Definitely 😂😂😂

Princess Van Renswoude

Buddy let’s check bank accounts !
Return to baggerdad

Roland Wells

Hey , you sound ridiculous. You probably support Trump. Before I block you, I just want to say, go away! 🤣🤣

Oliver Luoma

I’m just messing around with someone who is adamant about not caring, but here they are. It doesn’t matter to me what kind of work you do.

Oliver Luoma

If you were indifferent, you wouldn’t be putting in so much effort to argue your stance.

Roland Wells

Hower, you just keep going and going. I’m just playing along, but I am definitely better at it, especially when it comes to electrical work. Okay, I’m officially done with you now. I’ll just remove you from my comments. 😂😂

Roland Wells

If anyone replies to my comment with something silly, I’m just going to block them and move on with my day! 😂😂

Sienna Johnson

So, if Ryan erald didn’t follow those rules, then they would basically be fired, right? So, that still wouldn’t count as an exception. Like mentioned, the exception is for wiring that is continuous, unspliced, and not terminated through a junction box.

Dick Black

What are your thoughts on push-in wire connectors? My inspector gives them the green light, on the condition that they are only used for grounding wires between 12-20 gauge. No other applications.

Roland Wells

Wago connector your inspector is a wise man, indeed. While I would agree, personally I prefer wire nuts and twisted wires 😀

Dick Black

Twisted wires and nuts are my go-to as well. However, in the photo provided by OP, there’s less than an inch of wire sticking out of the box. To fix this and extend it, using a push-in connector would be ideal. Once the installation is complete, it would be protected. It’s definitely better than having to run another line of romex due to a short wire.

Dick Black

Anything Leviton is good with me.

Dörthe Reitz

Nah

Catherine Rousseau

Lever wagos rank higher than push-in connectors, but fall below twisted wires, wire nuts, and screw terminals.

Serenity Riley

I always make it clear to my team: leave a foot of wire or you’re out. That’s one of the first things I tell them.

Ethan Ross

I recently saw a post from someone in Europe talking about how they’re planning to make insulated ground a code requirement over there. Exciting stuff! 💁🏻‍♂️

Connor Russell

Armando, dude, maybe just stick to handyman jobs if you’re not familiar with the basic NEC code.

Roland Wells

Hey there, I’ve been an electrician longer than you’ve been around, kid. I’m a licensed contractor, so stop trolling and move along. 😳🙄🤣🤣

Roland Wells

And by the way, screw you and the horse you rode in on! 😳🙄🤣🤣

Just and only the new text: and by the way, screw you and the horse you rode in on! 😳🙄🤣🤣

Connor Russell

Ouch you really know how to hurt people’s feelings huh… ? Oh wait I think I hurt yours huh…! Lol all you had was a generic curse saying to try to insult me bro… 😅! You’re a fool..! Lol

Roland Wells

You’re the only fool, you don’t show your face because I’m sure your profile looks as silly as you sound 😳🤣🤣

Roland Wells

Get out of here with that trolling nonsense push it

Socorro de la Crúz

Those crimps are a pain for the next person who needs to come back and work on the box. I’ve been in the field for over 20 years and I’ve rarely used them outside of trade school.

علی رضا نكو نظر

Gave his consent.

Darío Cornejo

I’ve gotten pretty skilled at taking them off. I can usually wiggle them loose just right so they come off easily. And if it makes sense, I’ll reuse them again.

Melina Petković

Join the industry. ain at least 4 years of experience and then reconsider this question 🤦

Diana Zamora
Melina Petković

Nope . Put in the effort and figure it out like any other skilled tradesman. Come wear a tool belt and work alongside me, and I’d be more than happy to show you the ropes.

Melina Petković

😊. Who claimed I’m not learning? I’m learning every single day. If you’re not learning, you’re stagnant.

Eden Jones

I feel like people are really focusing on the crimps in this discussion, but the main issue here is the super short conductors. No matter which splicing method you choose, make sure your wires are at least 6 inches from the sheathing or extend 3 inches past the front of the box – whichever is longer. I’ve encountered this problem before and it’s frustrating to work on a box that’s wired this way, especially when you have to reconnect those extremely short grounds.

مهدي مرادی

I can’t stand ground crimps… use green wire nuts. Also, all grounds should extend 3 inches past the outside edge of the box, one of them 6 inches out from the edge, twisted, crimped, green wire nut, wire nut with a pigtail, lever Wago… whatever you prefer to use. Then push it to the back of the box. That’s how I do it and it’s code compliant

V

We typically leave 4 inches of wire outside the box. If you tuck it in properly, it should be fine.

Mücahid Mourik

You just require a SINLE ground wire to exceed 2” in length (minimum of 6” for it), however the others ought to terminate at the rear of the box.

Katherina Kortmann

Sorry, Ryan. You need to read the code.

Mücahid Mourik

Hey Wiley and Mike! Just a heads up, only one of your grounds should connect to the device, while the others should be attached to the box (or at the back of the box). I’m guessing you’re both following NEC, not CEC.

Katherina Kortmann

Make sure to leave at least 6 inches of free conductor at outlets, junctions, and switches for splices or connecting devices. If the opening is less than 8 inches, each conductor should extend at least 3 inches outside the opening. And remember, if the conductors are not spliced or terminated, they don’t have to follow this rule.

Mücahid Mourik

Hey , did you double-check that sentence before hitting send? It’s like I mentioned before, bare conductors that only need to reach the screws at the back of the box don’t have to follow the 6” rule. Just remember, in a single gang box, only one bare conductor needs to be 6” long. The others can be as short as you need them to be, as long as they reach the ground screws.

Katherina Kortmann

Make sure the cable is at least 3 inches long, unless you are terminating it directly into the receptacle – in that case, it needs to be 3 inches long. Keep in mind that a pass through or splice is the only exception.

Mücahid Mourik

‘s exception only applies if the wire is not being connected or cut off at the outlet or switch. If the wire is only going to the screws in the back of the box, it means it is not reaching the outlet or switch.

Katherina Kortmann

So basically, Ryan, if the conductor is being used in that device, it’s considered the exception. This means that if the circuit is not being used in the device.

Dorina Ruoff

Hey Ryan, just to clarify, the box is labeled as an outlet, not a receptacle. The wire is being terminated in the outlet.

Andre Nguyen

Remember, only one ground wire counts towards box fill 😂

Leevi Oja

I’ve dealt with houses that have wiring like that before, and it’s always a hassle. That’s why when I use those crimps, I make sure to leave the ground wires long enough so that the next person working on it can easily cut behind the crimp and have plenty of wire to work with.

رهام رضایی

People who cut corners and shoddy electricians are the ones who do this.

Scarlett Fowler

A bare ground wire is something you don’t want floating around. It looks like that one would lay back nicely.

Kaya Arslanoğlu

Whenever I needed to swap out the box, I made sure to keep all the wires long with a green wire nut and a deep box.

Darío Cornejo

This is how it’s done.

Michael Allen

I miss those green wire nuts

Sanna Friestad

There is limited space in the box.

Corinne Dubois

5 turns, remove the bad buddy, tough turn, Buchanan.

Zara King

No content

Sofia Pedersen

This is exactly why I avoid leaving loops, regardless of personal preferences.

Craig Jordan

I get your point, but at least there are ground wires in the box half the time when I arrive I don’t see anything not connected together or on the device

Darío Cornejo

Hey there, , remember to appreciate the good things in life!

Edward Singh

I come across this situation all the time. I always advise the guys to make the connection, push it into the back of the box before trimming the wires. Make sure to leave at least 6 inches of wire on everything. If any joint needs to be removed to connect the device, then it was done incorrectly. It’s more difficult and time-consuming to fight it back into the box while trying to put the device in. It’s really challenging to change old habits with some guys.

Nicoline Hansen

I still remember the time we crimped every box during a rough home installation back in 1998. Our boss instructed us to crimp like the picture showed. The inspector ended up failing the entire rough-in because the wires were not crimped at least 6 inches long. We had to raise every box in the 6,000 square foot house – it was a total nightmare.

Maanas Saha

I totally agree, I can’t stand working with wires that are too short. I’ve witnessed situations where only the hot and neutral wires are barely an inch out of the box from the old timers. It seems like they wired the plugs first and then pulled the wire as tightly as possible to connect the next one. What harm is there in having an extra 30 feet of wire for the entire job? It’s really difficult to fold two twisted grounds in the box

Raymond James

Do you need anything else? ood connection

Adosindo Fogaça

That’s something only foolish people would do.

Enora Henry

Use green or a wire nut of some sort. Just hack if you’re going to crimp

Youssef Drivenes

Come on, just solve the issue and stop whining, do I have to come pull you out of the hole.

Alan Fuller

Maybe not the best way to go about it, but definitely not a code violation.

Brent Fisher

That’s my approach as well.

Everalda Campos

That was a ridiculous mistake. I accidentally cut myself on a sharp Buchanan short corner. It’s so silly, but we’re fixing it now 😂

Everalda Campos

There are many different types of coffee available for purchase.

There are so many different kinds of coffee to choose from.

Everalda Campos

No content

Weronika Toft

Can’t stand those!

Sina Campos

That’s not new construction…… I haven’t seen orange peel in at least 15 years

Sina Campos

Wow……. and since it’s government-funded, they don’t prioritize code….. noted

William Pedersen

– You must be mistaken if you believe they don’t take code seriously. THAT’s how they earn their bonuses.

Sina Campos

Christopher the inspectors on government projects are a joke and you must be crazy if you think they care

William Pedersen

– You’d be surprised how many of them are just in it for the cushy job… I work with people who DESPISE the government, but absolutely LOVE their paychecks. 😂🤣 Hearing them speak in the conference rooms could be considered fraud.

Sina Campos

Christopher that’s what I meant. Super cushy (serious pay cut too) and no Fs to familiarize oneself with or be thorough

William Pedersen

– PS – Deciphering sarcasm through text can be quite challenging.

William Pedersen

Some folks are perfectly content with not having a ton of money. And if you dedicate enough time, your salary could double, your retirement savings could increase, and your job might become a breeze.

Sina Campos

They seriously need to create a font specifically for sarcasm, Christopher.

William Pedersen

I would use it all the time 😂🤣

Sina Campos

Hey Christopher, over the past few years I’ve been approached about switching to the dark side about 5 times. If I were to make the move, I’d be looking at a pay cut of around 60 to 70k a year to work in inspection.

Sina Campos

Your comment about improvement over time doesn’t really hold up, especially with the introduction of pay equity in certain areas.

William Pedersen

– As the older employees retire, many companies prefer to promote from within.

Sina Campos

Christopher once again… equity pay is based on equality. There’s no preferential treatment based on seniority, so everyone receives the same pay rate.

William Pedersen

– Sorry for the confusion earlier. I was talking about advancing in the hierarchy. Pay grades remain fixed. Equity pay is strictly based on equivalent grades.

Sina Campos

Christopher… as I mentioned before… whether you’re an inspector or an electrician, the pay is the same according to equity standards. So there’s no opportunity to move up within the inspector role with my level of experience.

William Pedersen

– The top earner here makes $202k.

Sina Campos

Christopher is either an inspector or an electrician.

William Pedersen

– I can’t remember his exact job title, but he’s the one in charge and decides whether to approve or deny variances.

Sina Campos

Hey Christopher, what’s your take on the CBO?

Dörthe Reitz

Hey , what kind of texture do you think everyone’s house has? It seems like orange peel to me.

Sina Campos

Hey Chance, looks like it’s all knockdown around here.

Mathys Philippe

Make sure to check the proof before making any payments! Prices range from R150 for 800 units to R450 for 2000 units. If you’re interested, feel free to send me a message.

Signe Olsen

Try pinching the crimp in the opposite direction to open it instead of cutting it off, that way you won’t lose any length. Crimps are designed to be used this way to maintain the full length.

Abigail Kowalski

I would guess it’s either a code violation or someone being rude on the job site.

Ninon Dufour

Come on over and be a part of Blue Hedge Market Solution! We’re all about guiding people towards financial freedom and early retirement. Our group promotes saving and investing smartly, building up various income streams, and securing a stable financial future for everyone.

Charlie Kowalski

I was always taught to leave a gap of 3 fingers from the box

Attila Lopez

This can be quite irritating, so please refrain from doing it.

Pamela Jimenez

Hey everyone, send me a message with your business name if you want a cool and original logo design! I’m in a creative mood and ready to get started.

Albert Otoole

Following 300.14, if the box is 3.5 inches deep, the conductors should be a minimum of 6.5 inches long. You need at least 6″ and 3″ past the box opening to comply.

Mücahid Mourik

For a single gang box, only one bare conductor needs to be attached. The others just need to be long enough to reach the ground screws. (Doesn’t apply to the box in the picture without ground strap/screws)

Albert Otoole

Hey Ryan, can you give me the code reference for that statement?

Dorina Ruoff

Does Ryan erald’s question only pertain to a single grounded conductor and a single ungrounded conductor?

Ana Warholm

Trash

Ramon Benítez

I can’t stand those things. I always opt for a green pass-thru wirenut… much better in my opinion.

Sara Sørensen

This doesn’t make any sense! Make sure there’s enough wire to work with!

Sabri Schwinn

I’ve encountered this issue too, and they’ve installed a ground crimp fitting. If I have to replace the box for any reason, all but one wire is either too long or too short. It makes reconnection difficult and non-compliant with the code.

283
0
Would love your thoughts, please comment.x
()
x