Is there at least one issue with the 200A Service with disconnect located outside next to the meter?

Asked by José Lugo
2 months ago
Last Updated: October 31, 2024

So, the deal is we’ve got a 200A service with the disconnect outside next to the meter. I’ve managed to spot at least one issue.

Related picture 1Related picture 2
Subscribe
Notify of

56 Comments
Oldest
Newest Most Voted
Inline Feedbacks
View all comments
Ryan Young

Installing a bushing with the secondary connector facing backwards can be a bit tricky.

Lester Flores

D – Although the antioxidant compound may not be required by code, it’s an industry standard that any skilled electrician would use

Lily Mitchelle

– a bushing is not required for this cable assembly.

Lester Flores

Seems like the lockring might be missing, but maybe not.

Lester Flores

No content

Lester Flores

Let me know when you want me to stop

Buse Ayaydın

Your post has a spelling error, it should be ‘at least’ instead of ‘at lease’. Also, remember to keep neutrals and grounds separate in the sub panel. There are 2 sets. I also notice the other issues highlighted by others, especially the SER wire in conduit without a SER clamp and the 3 loose 2/0 aluminum wires in the SER clamp. There are numerous issues here that would definitely not pass electrical inspection in Florida.

Georgia Kelley

Didn’t like it either. Being unattractive is one thing, but the other aspects are definitely not acceptable.

Buse Ayaydın

Oh, I totally missed that little detail. I think some of those things were not okay even back then. There’s definitely a lot of issues there in my opinion.

Buse Ayaydın

Hey , can you tell me where the sticker is located?

Elizabeth Taylor

Speaking of which, it should be ‘need TO BE separated’. 😉

Buse Ayaydın

Thanks Ed for pointing that out! I have good eyes but still slip up sometimes!

Elizabeth Taylor

Hey , we all feel that way. Nothing wrong with that!

Raul Jenkins

B – Make sure not to connect the neutral and ground at the sun-panel

Julio Gamboa

Didn’t notice the bonding screw…

Amanda Black

After the service is disconnected, bonding cannot occur in the . The subpanel is also incorrectly configured with the EC and neutral connected to the same bus.

Maya Roy

Maybe it’s because the lugs for the ground wire and neutral are physically touching.

Julio Gamboa

Kyle randys – Oh no, didn’t realize it landed next to the neutral 🤣🤣🤣

Carter Macdonald

Are you going to splice in the panel?

Rufino Regalado

Make sure to bond at the initial disconnect point, not at the sub panel.

Luz Parra

NEC 250.30(A)(1)(b)

Amanda Black

Doesn’t always come first. You can’t bond it after disconnecting the service.

Rufino Regalado

That is not the case in the Authority Having Jurisdiction where I work. It would not pass inspection if bonded after the service disconnect.

Amanda Black

Have the inspector refer to the code book. There is no mention of a ‘first means of disconnect’. It is not allowed to bond after the ‘service disconnect’.

Rufino Regalado

I have seen many inspections failed because the subpanel was bonded. Different Authorities Having Jurisdiction have their own regulations that may go beyond the NEC 🤙🏻

Amanda Black

A subpanel cannot be bonded because it comes after the service disconnect. The service disconnect can be located after an emergency disconnect, which should be the primary means of disconnecting.

Isabella Price

That panel is not looking good at all haha

Alexandra Cook

A – Hey, it looks like you’ve got the connector flipped around on the main panel

Elizabeth Taylor

It was later noted that tin Tune’s piece is from 2016 and related to item . And yes, item E is a must!

Chad Jennings

Tin Tune also has no water meter on the property.

Elizabeth Taylor

Hey, , to address your question about the breakers “popping”: No, that’s actually caused by something completely different than the neutral/ground bonding problem.

Julio Canales

There’s no anti-caulk gel or nolux

Johnny Holmes

Check for spelling and grammar errors

Johnny Holmes

Use ‘least’ instead of ‘lease’

Martín Monroy

E – The quality of workmanship seems subpar

Justine Clark

No content

Justine Clark

No content

Fátima Ruiz

C – Oh, there’s no bushing for the feeder cable at the sub-panel

Terrence Jones

Ensure ultralight and grounds are separated in the sub panel

Marilou Roy

No barriers present on line side terminals 230.62(C)

Gwendolyn Hunt

Is the ground welded to the box? Haha

Mauro Colunga

If you take a good look, you’ll notice a tiny hole and something that resembles The reen Crusties.

Jason Hicks

Are you starting with the spelling of “least” or what? Haha

Jason Hicks

You know, it would have been better to use a PVC male adapter at the main disconnect instead of a backwards x connector. Also, don’t forget to put a plastic bushing on the 2″ x connector at the sub panel.

Kyle Reyes

I noticed the ground bar, it looks great, tidy, well done, keep it up!

Lee Arnold

Just go back to sleep, man.

Felix Orta

There is nothing intelligent about this!!!

Elmer Long

Second picture, NM connector installed incorrectly with missing bushing, bonding screw also missing. First image, ground and neutral are incorrectly bonded in the distribution panel with a missing bushing on the feeder wires and a double tab in the neutrals

Alfred Evans

Both panels are in great shape! Keep up the good work!

Logan Wong

Make sure to check your grammar

Noelle Gonzalez

If that panel is not back to back with the meter/main, then separate the grounds and neutrals inside

Citlali Zúñiga

That panel is a mess. Cables coming in through the same opening as the service entrance are not allowed in Canada. The wiring is a disaster…

Seeing things like this makes me appreciate my own work even more.

I would feel really sloppy if this was the job I had completed.