Have you ever required a 4 copper jumper to bond the neutral to the electrode ground, or do you typically bond it to the can or use a separate ground bar in the panel?

Asked by Gwendolyn Horton
4 months ago
Last Updated: September 10, 2024

Hey, do you usually use a #4 copper jumper to connect the neutral to the ground electrode? I usually bond the can or use a separate ground bar in the panel instead.

Related picture 1Related picture 2Related picture 3Related picture 4
Subscribe
Notify of

35 Comments
Oldest
Newest Most Voted
Inline Feedbacks
View all comments
Beth Long

Which code cycle are you following in your area?

Bob Garrett

#6 is the largest size required for a ground rod.

Owen Ambrose

I’m not entirely sure what you’re getting at here. The rounding Electrode Conductor size is determined from table 250.66 based on the service conductor size. For a 200A service using 4/0 aluminum conductors, yes, a 4 AW copper EC is necessary. And the EC SHOULD be connected to the grounded (neutral) conductor. The EC MAY be connected to the equipment grounding conductor terminal if a wire type main bonding jumper sized according to table 250.102(C)(1) is installed between the EC terminals and the grounded conductor terminals. For the same 200A service with 4/0 aluminum conductors, yes, a 4 AW copper MBJ is needed for this.

Antonio Graves

And for EC to ground rods only, 6 is the largest required.

Owen Ambrose

That’s accurate.

Owen Ambrose

Only if the EC connects solely to rod, pipe, or plate electrodes or any combination of those. If the EC also connects to any other type of electrode that requires a larger conductor, 6 AW is not the largest required.

Amelia Wallace

Additional grounding electrode conductor is a number six, which is the largest for the ground rods only. It doesn’t matter what size service it is. Now, the grounding electrode conductor that will, let’s say, connect to the copper water main is based on the size of the service entrance conductors. As mentioned earlier, if it’s a 200 amp service with 4/0 service entrance conductors, the grounding electrode conductor would be #4 THHN or bare

Antonio Graves

I haven’t run to rods and then on to more. Always a separate run

Antonio Graves

Connecting hot to ground in the panel, or EC to electrodes based on table …

6 is the biggest size needed for ground rods

I will need to check the size for the main bonding jumper

Antonio Graves

200 Amp

Antonio Graves

I’ve never installed the meter can. I either use a meter main outside or run the ground inside

Antonio Graves

When a fault occurs…

Antonio Graves

Can carry the ground. Not neutral bond

Antonio Graves

No content

Aubree Gauthier

The attachment point in the picture definitely doesn’t seem to be 12 feet away.

Cecil Hall

Also the weather head should be above the POA, there are exceptions but they don’t apply here

Owen Ambrose

It just needs to be 10′

Cecil Hall

No worries at all. You probably won’t! I often see small issues like that, but overall, it looks pretty good. I typically use SE cable as it blends in better than pipe. Some services may require pipe, but personally, I would have chosen SE for this job.

Cecil Hall

I get what you’re saying. When I look at those images, the existing SE cable doesn’t appear to be in bad shape. It’s likely over 30 years old at this point, but with the conduit, it should last much longer.

Catherine Gomez

Trading cryptocurrency successfully in the current bear market requires both experience and a solid strategy. That’s why I rely on the trusted and profitable signals provided by Mrs. Laura Andreas. Since joining her platform, I have made significant profits using her easy-to-implement trading strategy. For more information, feel free to contact her at 📥📥📥◀️ Laura Andreas

Maeva Wong

According to Code Number 6, two grounding rods are required for earthing, with a continuous wire.

Ryder Gagnon

Yes number 4 on a 2-meter service. Those are both 100 amp sockets, (200 amp. Capacity) and the AHJ will not accept bonds as continuity.
Direct connection in this situation.

Ryder Gagnon

Hey Rob, I have been following this practice on my projects for 40 years.